  1. D

    TIA KTP900F E-Stop PROFIsafe Betriebsmodus Verbindungsprobleme

    The issue was rectified by replacing the Connection Box :)
  2. D

    TIA KTP900F E-Stop PROFIsafe Betriebsmodus Verbindungsprobleme

    yes this is the safety program
  3. D

    TIA KTP900F E-Stop PROFIsafe Betriebsmodus Verbindungsprobleme

    How to rectify this issue , does this makes problem ?
  4. D

    TIA KTP900F E-Stop PROFIsafe Betriebsmodus Verbindungsprobleme

    i made new settings both in TIA hw configuration and panel side.
  5. D

    TIA KTP900F E-Stop PROFIsafe Betriebsmodus Verbindungsprobleme

    Yes , i have changed the device name and profisafe address in hw config
  6. D

    TIA KTP900F E-Stop PROFIsafe Betriebsmodus Verbindungsprobleme

    Unfortunately, I'm still having communication issues; the runtime won't start. After downloading the project, the runtime on the KTP900F mobile panel stops. The rotary switch setting was configured as 0A, but the mobile panel does not accept 10 as a decimal value and displays an error in the...
  7. D

    TIA KTP900F E-Stop PROFIsafe Betriebsmodus Verbindungsprobleme

    Entschuldigung, es waren 900F
  8. D

    TIA KTP900F E-Stop PROFIsafe Betriebsmodus Verbindungsprobleme

    @DeltaMikeAir Vielen Dank für Ihre Hilfe! Ich hatte die Adresse falsch verstanden. Dank Ihrer Klarstellung weiß ich jetzt, dass die Anschlussbox tatsächlich die Adresse 160 (HEX A0) hat. Ich weiß Ihre Unterstützung wirklich zu schätzen!"
  9. D

    TIA KTP900F E-Stop PROFIsafe Betriebsmodus Verbindungsprobleme

    Support-Anfrage: KTP900F E-Stop PROFIsafe Betriebsmodus Verbindungsprobleme Problemübersicht: Wir haben Probleme mit dem KTP900F E-Stop PROFIsafe Betriebsmodus in Bezug auf die Verbindung zur Anschlussbox. Die Probleme treten weiterhin auf, obwohl die Konfigurationseinstellungen den erwarteten...