Solved. Thanks a lot.
I have mistaken the RS232-to-422/485 convertor as the old fashion one in which one has to tied up the (TXD+, RXD+) and (TXD-, RXD-) together to get RS485. The new fashion one that I used just needed T/RXD+ and T/RXD- for the A,B lines of RS485.
A Chinese RS232-to-RS485 adapter using COM 1 on a Dell D520 laptop.
I could monitor the serial com with a serial com monitoring device.
There was no answer from the VLT 2800. It happened on both the old and new VLT 2800.
I suspected there should be something related to the parameters setup or...
I have VLT2800 which needs replacement. I have installed MCT10 V3.17 and RS485 driver to connect to VLT2800 to dump its configuration data.
Have checked that VFD parameters are as follows:
500 [1] Address = 1
501 [5] baud rate = 9600
512 [1] FC telegram
561 [0] FC protocol
Tried terminals 68, 69...
I solved the problem.
The problem was the com port of IBM T30 notebook did not give DTR signal.
I tried with Siemens PG740 with the same cable and same software.
I could do the readback with PCSPRO 5.8. PCSPRO 5.8 did the auto serial port settings.
Thank you for all your help.
Best regards,
KK
Dear All,
I got message "PCS doesn't reply! Please check connection to COM1" when doing readback operation in PCSPRO for PCS095.
I have checked my PCS733 cable. It was ok pin-to-pin. Are there any dip switches to be set or any keys to be pushed to put the PCS095 into programming mode for...