    I am new to Phoenix (coming from S7 - and it looks like I'm quickly returning).

    The controller is a 3050 (don't have it here - running simulator), and as far as I've understood, it is quite capable.
    The HMI is Schneider IGSS and the protocol is OPC-UA.

    I'm using the CTRL_PID function from Oscat. I can address the input variables directly from IGSS.
    But the parameter settings are of course input_var's that CANNOT BE HOOKED AS RETAIN IN PCWORX. Why is this not allowed? Wake up you developers!
    Guess what happens after a cold start.

    Do I need to pack the controller in my own FB with triplicated parameters?
    MyFBInputs ->Update if 0 -> MyFBOutputs (Retain) -> CTRL-inputs!

    Any better solutions?

    Kaputt
    Zitieren Zitieren PCWORX and retain values  

  2. #2
    Registriert seit
    08.09.2010
    Ort
    Blomberg
    Beiträge
    423
    Danke
    1
    Erhielt 66 Danke für 63 Beiträge

    Standard

    Hello kaputt,

    normally you can mark nearly all variables as retain, even when they're an input to a FB or FC.

    But you've keep in mind when you're using a global Variable that the option is only available in the global Variable sheet.
    In the local Variable sheet the Variable is than marked as "Var_External" (somekind of pointer to the global with the same name) and all options are grey.

    In case this is not the solution I need to know more about the application, maybe a screenshot of the variable may help.

    Of course you can call also our free automation hotline +4952819462888

    Greetings

    Frank

    call number 72766
    PHOENIX CONTACT Deutschland GmbH
    Hotline: 05281-946-2888
    automation-service@phoenixcontact.com
    www.phoenixcontact.de

  3. #3
    kaputt ist offline Benutzer
    Themenstarter
    Registriert seit
    26.12.2009
    Beiträge
    98
    Danke
    22
    Erhielt 9 Danke für 7 Beiträge

    Standard


    Zuviel Werbung?
    -> Hier kostenlos registrieren
    Thanks for the reply!

    I'll make a screenshot when I'm back in office after the Pingst.

    In the mean time I've made a 'mother' FB that calls a modified Oscat CTRL-FB (Input_Var are changed to Var with 'Retain'). The 'mother' has got the initial input_var parameters from her instance call and they are copied to the CTRL -var's when it is detected that a new instance is downloaded ( = if the gain is 0). This is not a bad solution.

    I am not familiar with the Phoenix CPU behavior, and I am not keen of being the 'hero of the day' by resetting all parameters during production when I do a simple program change/download.

    The clue is not to find out what a new system can do, but what it cannot.

    MfG
    Kaputt

Ähnliche Themen

  1. [Libnodave] Force values
    Von MrChiliCheese im Forum Hochsprachen - OPC
    Antworten: 0
    Letzter Beitrag: 09.07.2014, 21:07
  2. DotNetSiemensPLCToolBoxLibrary - Write Values Update...
    Von Jochen Kühner im Forum Hochsprachen - OPC
    Antworten: 0
    Letzter Beitrag: 24.05.2012, 18:05
  3. PCWORX Problem
    Von Step7Neuling im Forum Sonstige Steuerungen
    Antworten: 6
    Letzter Beitrag: 04.11.2011, 06:29
  4. Hilfe PcWorX
    Von manf im Forum Programmierstrategien
    Antworten: 2
    Letzter Beitrag: 06.05.2008, 10:21
  5. Skalierungsproblem mit FC105 "Scaling Values"
    Von dummyuser im Forum Simatic
    Antworten: 3
    Letzter Beitrag: 02.10.2006, 18:59

Lesezeichen

Berechtigungen

  • Neue Themen erstellen: Nein
  • Themen beantworten: Nein
  • Anhänge hochladen: Nein
  • Beiträge bearbeiten: Nein
  •