Hello together,

We have trouble with the profinet to PLC S7-1214C

General:
The profinet connection is running with the standard default mapping. We don´t use the fieldbus mapping tool inside the CVIPC2000 engineering tool

  • The problem is following:
    1. The profinet is working.
    2. After the power on time, the plc can't find the device name (profinet) desoutter unit!

The screen shot shows: everything ok and the station is working.
pic_Net_running.jpg
We have following situation after the power on time:
Net_down_after_power_on.jpg
Net_down_after_power_on1.jpg
Here can you see the loosing NAME DEVICE: Why loosed the desoutter device his Device Name?

Net_run_assign_Name.jpg
pic_Net_running1.jpg

Desoutter said me: the problem come from Siemens!
Have somebody the same situation?

Thanks a lot

Tobias Hammer


 
Zuletzt bearbeitet:
Hello,
in the Desoutter Software CVIPC 2000 is a field with the name "station comment" this is the "profinet name" for Desoutter. Do not use _ in the "profinet name" the Desoutter profinet modul cant work with underlines.

Hope i can help.
 