B&R System2003, Profibusanbindung

Zuviel Werbung?
-> Hier kostenlos registrieren
In dem B&R Modul ist ein ASIC SPC3 verbaut, laut Chip Hersteller (Siemens):
6.2.5 Write_Read_Data / Data_Exchange (Default_SAP)
Auszug:
If the user’s evaluation cycle time is shorter than the bus cycle time, the user does not find any new buffers

with the next ‘Next_Dout_Buffer_Cmd’ in ‘N.’ Therefore, the buffer exchange is omitted, At a 12 Mbd baud

rate, it is more likely, however, that the user’s evaluation cycle time is larger than the bus cycle time. This

makes new output data available in ‘N’ several times before the user fetches the next buffer. It is

guaranteed, however, that the user receives the data last received.

Könnte die Zykluszeit auf der B&R Seite etwas damit zu tun haben?
 
In dem B&R Modul ist ein ASIC SPC3 verbaut, laut Chip Hersteller (Siemens):
6.2.5 Write_Read_Data / Data_Exchange (Default_SAP)
Auszug:
If the user’s evaluation cycle time is shorter than the bus cycle time, the user does not find any new buffers

with the next ‘Next_Dout_Buffer_Cmd’ in ‘N.’ Therefore, the buffer exchange is omitted, At a 12 Mbd baud

rate, it is more likely, however, that the user’s evaluation cycle time is larger than the bus cycle time. This

makes new output data available in ‘N’ several times before the user fetches the next buffer. It is

guaranteed, however, that the user receives the data last received.

Könnte die Zykluszeit auf der B&R Seite etwas damit zu tun haben?
Das geht am Problem vorbei. Die Karte ist noch nicht im Datenaustausch.

Nach einer Änderung von param muss die CPU (CP474) übrigens neu gestartet werden.
 
Zurück
Oben