Versa-Point GSD-file
;**************************************************************
; GSD-File for VersaPoint PROFIBUS-DP NETWORK INTERFACE UNIT
; Manufacturer : GE Intelligent Platforms
; Article-No. : IC220PBI001-AA
; Hardware-Release : 02
; Firmware-Release : B (42 hex)
; GSD-Revision : 1.07
; Date : 24.09.2013
;**************************************************************
;****************** Changes ***********************************
; Date Change
; 1.00 -initial product release
; 1.01 -corrected entry for 2ch analog output module
; 1.02 -new modules added
; 1.03 -new modules added, module discription changed
; 1.04 -NIU parameter definitions added
; 1.05 -VersaSafe added
; 1.06 -VersaPoint Modules added (CNHYIIO00452 release)
; 1.07 -VersaSafe Phase 2 release
;**************************************************************
#Profibus_DP
GSD_REVISION = 2 ; version ID of the GSD file format
Vendor_Name = "GE Intelligent Platforms" ; manufacturer name
Model_Name = ""VersaPoint Profibus NIU (DIP8=OFF)" ; device name
Revision = "V2.0" ; device revision
Ident_Number = 0x05B9 ; product ID
Slave_Family = 3 ; device family class
Protocol_Ident = 0 ; protocol ID of the device
Station_Type = 0 ; device type
FMS_supp = 0 ; no DP/FMS mixed device
Hardware_Release = "V2.0" ; hardware revision
Software_Release = "B" ; software revision
Bitmap_Device = "GEF05B9N" ; device bitmap - normal state
;Bitmap_Diag = "GEF05B9D" ; device bitmap - diagnostic state
;Bitmap_SF = "GEF05B9N" ; device bitmap - special (passive) state
9.6_supp = 1 ; supported baudrates
19.2_supp = 1
45.45_supp = 1
93.75_supp = 1
187.5_supp = 1
500_supp = 1
1.5M_supp = 1
3M_supp = 1
6M_supp = 1
12M_supp = 1
MaxTsdr_9.6 = 15 ; device respond times
MaxTsdr_19.2 = 15
MaxTsdr_45.45 = 15
MaxTsdr_93.75 = 15
MaxTsdr_187.5 = 15
MaxTsdr_500 = 15
MaxTsdr_1.5M = 25
MaxTsdr_3M = 50
MaxTsdr_6M = 100
MaxTsdr_12M = 200
Redundancy = 0 ; no redundancy
Repeater_Ctrl_Sig = 2 ; RTS available
Modul_Offset = 0 ; 1. Slot number for HW config tool
;**************************************************************
;********* modular device *********************************
;**************************************************************
Modular_Station = 1 ; modular device
Max_Module = 63 ; max 63 modules
Max_Input_Len = 184 ; max 184 Byte input data
Max_Output_Len = 184 ; max 184 Byte output data
Max_Data_Len = 184 ; max sum: 184 Byte input and output data
;*******************************************MaxTsdr_45.45 = 15*******************
;*** Parameter Text Definitions *****************************
;**************************************************************
PrmText = 1
Text(0) = "Local Bus: Run"
Text(1) = "Local Bus: Stop"
EndPrmText
PrmText = 2
Text(0) = "automatically"
Text(1) = "manually"
EndPrmText
PrmText = 3
Text(0) = "Byte 0-1 = Plug 4/3-2/1"
Text(1) = "Byte 0-1 = Plug 2/1-4/3"
EndPrmText
PrmText = 4
Text(0) = "On Global Control Operate only"
Text(1) = "Without Global Control Operate"
EndPrmText
PrmText = 5
Text(0) = "Byte 0/1/2/3 = Plug 4/3/2/1"
Text(1) = "Byte 0/1/2/3 = Plug 1/2/3/4"
EndPrmText
;**************************************************************
;*** Parameter Data Options and Positions *******************
;**************************************************************
ExtUserPrmData = 1 "Station Behaviour on Errors"
Bit(0) 0 0-1
Prm_Text_Ref = 1
EndExtUserPrmData
ExtUserPrmData = 2 "Acknowledge of peripheral Faults"
Bit(1) 0 0-1
Prm_Text_Ref = 2
EndExtUserPrmData
ExtUserPrmData = 3 "DI16/DO16 byte position"
Bit(4) 0 0-1
Prm_Text_Ref = 3
EndExtUserPrmData
ExtUserPrmData = 4 "Data Exchange Mode"
Bit(5) 1 0-1
Prm_Text_Ref = 4
EndExtUserPrmData
ExtUserPrmData = 5 "DI32/DO32 byte position"
Bit(6) 0 0-1
Prm_Text_Ref = 5
EndExtUserPrmData
;**************************************************************
;********* slavespecific data *****************************
;**************************************************************
Freeze_Mode_supp = 1 ; device supports freeze mode
Sync_Mode_supp = 1 ; device supports sync mode
Auto_Baud_supp = 1 ; automatic baud rate recognition
Min_Slave_Intervall = 2 ; min cycle time 0.2ms
Max_Diag_Data_Len = 16 ; max length of diagnostic data
Max_User_Prm_Data_Len = 1 ; length of User_Prm_Data
Ext_User_Prm_Data_Const(0) = 0x20 ; 1 Byte for coupler parameter
Ext_User_Prm_Data_Ref(0) = 1
Ext_User_Prm_Data_Ref(0) = 2
Ext_User_Prm_Data_Ref(0) = 3
Ext_User_Prm_Data_Ref(0) = 4
Ext_User_Prm_Data_Ref(0) = 5
;********* PD-PCP (VC1) ******************************
Module="PD-PCP 4 words" 0xF3
EndModule
Module="PD-PCP 6 words" 0xF5
EndModule
Module="PD-PCP 8 words" 0xF7
EndModule
Module="PD-PCP 10 words" 0xF9
EndModule
Module="PD-PCP 12 words" 0xFB
EndModule
Module="PD-PCP 14 words" 0xFD
EndModule
Module="PD-PCP 16 words" 0xFF
EndModule
;********* digital output modules **************************
Module="IC220MDL930*OUT RELAY 3A 1PT" 0x82,0x00,0xBD,0xC2
EndModule
Module="IC220MDL940*OUT RELAY 3A 4PT" 0x82,0x00,0xBD,0x41
EndModule
Module="IC220MDL931*OUT RELAY 3A PC 1PT" 0x82,0x00,0xBD,0xC2
EndModule
Module="IC220MDL941*OUT RELAY 3A PC 4PT" 0x82,0x00,0xBD,0x41
EndModule
Module="IC220MDL350*OUT VAC 0.5A 1PT" 0x82,0x00,0xBD,0xC2
EndModule
Module="IC220MDL350*OUT VAC 1A 4PT" 0x82,0x00,0xBD,0x41
EndModule
Module="IC220MDL751*OUT 24VDC .5A 2PT" 0x82,0x00,0xBD,0xC2
EndModule
Module="IC220MDL721*OUT 24VDC 2A 2PT" 0x82,0x00,0xBD,0xC2
EndModule
Module="IC220MDL761*OUT 24VDC NEG 2PT" 0x82,0x00,0xBD,0xC2
EndModule
Module="IC220MDL771*OUT 24VDC DIAG 2PT" 0xC2,0x00,0x00,0xBF,0x41
EndModule
Module="IC220MDL752*OUT 24VDC .5A 4PT" 0x82,0x00,0xBD,0x41
EndModule
Module="IC220MDL753*OUT 24VDC .5A 8PT" 0x82,0x00,0xBD,0x81
EndModule
Module="IC220MDL723*OUT 24VDC 2A 8PT" 0x82,0x00,0xBD,0x81
EndModule
Module="IC220MDL754*OUT 24VDC .5A 16PT" 0x82,0x01,0xBD,0x01
EndModule
;********* digital output modules, packed ******************
Module="OUT RELAY 1PT QTY.2/4Bit" 0x83,0x00,0xBD,0xC2,0x02
EndModule
Module="OUT RELAY 1PT QTY.3/6Bit" 0x83,0x00,0xBD,0xC2,0x03
EndModule
Module="OUT RELAY 1PT QTY.4/8Bit" 0x83,0x00,0xBD,0xC2,0x04
EndModule
Module="OUT RELAY 4PT QTY.2/8Bit" 0x83,0x00,0xBD,0x41,0x02
EndModule
Module="OUT VAC 1PT QTY.2/4Bit" 0x83,0x00,0xBD,0xC2,0x02
EndModule
Module="OUT VAC 1PT QTY.3/6Bit" 0x83,0x00,0xBD,0xC2,0x03
EndModule
Module="OUT VAC 1PT QTY.4/8Bit" 0x83,0x00,0xBD,0xC2,0x04
EndModule
Module="OUT VAC 4PT QTY.2/8Bit" 0x83,0x00,0xBD,0x41,0x02
EndModule
Module="OUT 24VDC POS/NEG 2PT QTY.2/4Bit" 0x83,0x00,0xBD,0xC2,0x02
EndModule
Module="OUT 24VDC POS/NEG 2PT QTY.3/6Bit" 0x83,0x00,0xBD,0xC2,0x03
EndModule
Module="OUT 24VDC POS/NEG 2PT QTY.4/8Bit" 0x83,0x00,0xBD,0xC2,0x04
EndModule
Module="OUT 24VDC POS 4PT QTY.2/8Bit" 0x83,0x00,0xBD,0x41,0x02
EndModule
;********* digital input modules ***************************
Module="IC220MDL220*IN 120VAC 1PT" 0x42,0x00,0xBE,0xC2
EndModule
Module="IC220MDL230*IN 230VAC 1PT" 0x42,0x00,0xBE,0xC2
EndModule
Module="IC220MDL641*IN 24VDC 2PT" 0x42,0x00,0xBE,0xC2
EndModule
Module="IC220MDL661*IN 24VDC NEG 2PT" 0x42,0x00,0xBE,0xC2
EndModule
Module="IC220MDL651*IN 24VDC 2PT DESINA" 0x42,0x00,0xBE,0x41
EndModule
Module="IC220MDL642*IN 24VDC 4PT" 0x42,0x00,0xBE,0x41
EndModule
Module="IC220MDL643*IN 24VDC 8PT" 0x42,0x00,0xBE,0x81
EndModule
Module="IC220MDL644*IN 24VDC 16PT" 0x42,0x01,0xBE,0x01
EndModule
;********* digital input modules, packed *******************
Module="IN 120/230VAC 1PT QTY.2/4Bit" 0x43,0x00,0xBE,0xC2,0x02
EndModule
Module="IN 120/230VAC 1PT QTY.3/6Bit" 0x43,0x00,0xBE,0xC2,0x03
EndModule
Module="IN 120/230VAC 1PT QTY.4/8Bit" 0x43,0x00,0xBE,0xC2,0x04
EndModule
Module="IN 24VDC POS/NEG 2PT QTY.2/4Bit" 0x43,0x00,0xBE,0xC2,0x02
EndModule
Module="IN 24VDC POS/NEG 2PT QTY.3/6Bit" 0x43,0x00,0xBE,0xC2,0x03
EndModule
Module="IN 24VDC POS/NEG 2PT QTY.4/8Bit" 0x43,0x00,0xBE,0xC2,0x04
EndModule
Module="IN 24VDC POS 4PT QTY.2/8Bit" 0x43,0x00,0xBE,0x41,0x02
EndModule
;********* analog output modules **************************
Module="IC220ALG320*ALG OUT V/C 1CH" 0x82,0x40,0x7D,0x01
EndModule
Module="IC220ALG321*ALG OUT V 1CH" 0x82,0x40,0x7D,0x01
EndModule
Module="IC220ALG322*ALG OUT V 2CH" 0xC2,0x41,0x41,0x5B,0x02
EndModule
;********* analog input modules ****************************
Module="IC220ALG220*ALG IN V/C 2CH" 0xC2,0x41,0x41,0x7F,0x02
EndModule
Module="IC220ALG221*ALG IN V/C 8CH" 0xC2,0x41,0x41,0x5F,0x02
EndModule
Module="IC220ALG620*ALG IN RTD 2CH" 0xC2,0x41,0x41,0x7F,0x02
EndModule
Module="IC220ALG630*ALG IN THM 2CH" 0xC2,0x41,0x41,0x7F,0x02
EndModule
;********* power-level terminals **************************
Module="IC220MDD850*IN THERMISTOR 1PT" 0x42,0x00,0xBE,0x41
EndModule
Module="IC220STR001*MSTR DIR 1.5KW/400" 0xC2,0x00,0x00,0xBF,0x81
EndModule
Module="IC220STR003*MSTR REV 1.5KW/400" 0xC2,0x00,0x00,0xBF,0x81
EndModule
Module="IC220STR002*MSTR DIR 3.7KW/400" 0xC2,0x00,0x00,0xBF,0x81
EndModule
;********* special function modules ***********************
Module="IC220MDD840*HSC 1IN/1OUT 24VDC" 0xC2,0xC1,0xC1,0xBF,0x02
EndModule
Module="IC220MDD842*INC ENC IN 24VDC" 0xC2,0xC1,0xC1,0xBF,0x02
EndModule
Module="IC220MDD841*ABS ENC IN 24VDC" 0xC2,0xC1,0xC1,0xBF,0x02
EndModule
Module="IC220BEM232*SER COMM RS232 1CH" 0xC2,0xC0,0xC0,0xDC,0x01
EndModule
Module="IC220BEM485*SER COMM RS485 1CH" 0xC2,0xC0,0xC0,0xDC,0x01
EndModule
;********* power- and segment terminals *******************
Module="IC220PWR003*PWR TERM F-D 24VDC" 0x42,0x00,0xBE,0xC2
EndModule
Module="IC220PWR013*SEG TERM F-D 24VDC" 0x42,0x00,0xBE,0xC2
EndModule
Module="IC220PWR014*SEG TERM ELF 24VDC" 0x42,0x00,0xBE,0xC2
EndModule
;********* Safety Bridge modules ***************************
Module="IC220SDL963*ENH LPSDO 24W SBT" 0xC2,0xD7,0xD7,0xAB,0x18
EndModule
Module="IC220SDL953*LPSDO MUX SBT V2" 0xC2,0xC7,0xC7,0xAB,0x08
EndModule
Module="IC220SDL953*LPSDO 16W SBT V2" 0xC2,0xCF,0xCF,0xAB,0x10
EndModule
Module="IC220SDL953*LPSDO 24W SBT V2" 0xC2,0xD7,0xD7,0xAB,0x18
EndModule
Module="IC220SDL543*PSDI 8 IN SBT" 0xC2,0xC3,0xC3,0xA3,0x04
EndModule
Module="IC220SDL544*PSDI 16 IN SBT" 0xC2,0xC3,0xC3,0xA3,0x04
EndModule
Module="IC220SDL753*PSDO 8 OUT SBT" 0xC2,0xC3,0xC3,0xA7,0x04
EndModule
Module="IC220SDL840*PSDOR 4 OUT SBT" 0xC2,0xC3,0xC3,0xA7,0x04
EndModule
Module="IC220SDL752*PSDO 4/4 OUT SBT" 0xC2,0xC3,0xC3,0xA7,0x04
EndModule
;********* VersaPoint High density modules *****************
Module="IC220MDL765*OUT 24VDC 8PT" 0x82,0x00,0xBD,0x81
EndModule
Module="IC220MDL665*IN 24VDC 8PT" 0x42,0x00,0xBE,0x81
EndModule
Module="IC220ALG330*ALG OUT V/C 2CH" 0xC2,0x43,0x43,0x5B,0x04
EndModule
Module="IC220ALG231*ALG IN V 4CH" 0xC2,0x43,0x43,0x7F,0x04
EndModule
Module="IC220ALG230*ALG IN I 4CH" 0xC2,0x43,0x43,0x7F,0x04
EndModule
Module="IC220MDD843*OUT 5/24VDC PWM/PT 2CH" 0xC2,0xC1,0xC1,0xBF,0x02
EndModule
;********* VersaMax IP modules ******************************
Module="IC677DBO085*OUT 24VDC 8PT" 0x82,0x00,0xBD,0x81
EndModule
Module="IC677DBI008*IN 24VDC 8PT" 0x42,0x00,0xBE,0x81
EndModule
Module="IC677DBM442*IN/OUT 24VDC 4/4PT" 0xC2,0x00,0x00,0xBF,0x41
EndModule
Module="IC677ABO004*ALG OUT V/C 4CH" 0xC2,0xC4,0xC4,0xDF,0x05
EndModule
Module="IC677ABI004*ALG IN V/C 4CH" 0xC2,0xC4,0xC4,0xDF,0x05
EndModule
;**************************************************************
;********* device diagnostics *****************************
;**************************************************************
;**************************************************************
;********* PROFIBUS standard diagnostics ******************
; Byte 0 station state 1
; Byte 1 station state 2
; Byte 2 station state 3
; Byte 3 PROFIBUS master address
; Byte 4 00H (manufacturers ID high Byte)
; Byte 5 F0H (manufacturers ID low Byte)
;**************************************************************
;**************************************************************
;********* device specific diagnostics ********************
;**************************************************************
; Byte 6 0AH (Header Byte, number of following byte)
; Byte 7 00H (type of diagnostics)
; Byte 8 firmware revision, ASCII coded
; Byte 9 error type
; Byte 10 error number
; meaning of error type-error number:
; 1: parameterization error PROFIBUS
; 1-1: wrong slot number
; 1-2: parameter block (failsafe or configuration) is incomplete
; 1-3: data length of a parameter block is too small
; 1-4: data length of a parameter block is too large
; 1-5: internal block length (failsafe and configuration) is too small
; 1-6: header byte of parameterblock is incorrect
; 1-7: PCP-initialization for a module without PCP functionality
; 1-8: too many data blocks for the module
; 1-9: incomplete parameter data of inactive Module
; 2: configuration error PROFIBUS
; 2-1: less modules configured than connected
; 2-2: less modules connected than configured
; 2-3: 1st byte of special signature format is incorrect
; 2-4: for last module not enough byte of special signature format configured
; 2-5: sum of configured process data > 176 byte
; 2-6: different ID codes for configuration and module
; 2-7: different length codes for configuration and module
; 2-8: number of manufacturer specific data is incorrect
; 2-9: not enough output byte configured
; 2-10: not enough input byte configured
; 2-11: configuration of PROFIBUS needs more than 244 byte
; 2-12: internal list too small
; 2-13: too little output byte for inactive module
; 2-14: too little input byte for inactive module
; 3: configuration error INTERBUS Inline station
; 3-1: module type not allowed
; 3-2: module length code zero not allowed
; 3-3: module length code > 32 byte not allowed
; 3-4: Loop1 module not allowed
; 3-5: sum of INTERBUS process data too large (>176 Byte)
; 3-6: more than 64 modules connected
; 3-7: sum of PROFIBUS process data > 176 Byte
; 3-8: more than 8 PCP devices connected
; 4: INTERBUS error
; 4-1: local bus error (Data In)
; 4-2: local bus error (Data Out)
; 4-3: error can not be localized
; 4-4: INTERBUS Inline module not ready
; 4-5: new INTERBUS module has an incorrect length- or ID-code
; 4-6: additional INTERBUS Inline module(s) connected
; 5: module error
; 5-1: peripheral fault
; 5-2: Module not ready
; 6: parameterization error local bus
; 6-1: pcp initiate telegram could not be sended
; 7: EEPROM fault
; 7-1: no EEPROM
; 7-2: checksum error
; 7-3: EEPROM read error
; 7-4: EEPROM write error
; 7-5: EEPROM initialized
; 7-6: difference between EEPROM configuration and real configuration
; Byte 11 device number 1 (INTERBUS Inline module)
; Byte 12 device number 2 (INTERBUS Inline module)
; Byte 13 INTERBUS Inline ID code
; Byte 14 INTERBUS Inline length code
; Byte 15 reserved
;**************************************************************
;******** error type **************************************
Unit_Diag_Area = 16-23
Value(1) = "#1-parameter error PROFIBUS"
Value(2) = "#2-PROFIBUS configuration error"
Value(3) = "#3-INTERBUS configuration error"
Value(4) = "#4-INTERBUS error"
Value(5) = "#5-module error"
Value(6) = "#6-parameter error local bus"
Unit_Diag_Area_End
;******** error number ************************************
Unit_Diag_Area = 24-31
Value(1) = "Error number: #1"
Value(2) = "Error number: #2"
Value(3) = "Error number: #3"
Value(4) = "Error number: #4"
Value(5) = "Error number: #5"
Value(6) = "Error number: #6"
Value(7) = "Error number: #7"
Value(8) = "Error number: #8"
Value(9) = "Error number: #9"
Value(10) = "Error number: #10"
Value(11) = "Error number: #11"
Unit_Diag_Area_End
;******** error location start ****************************
Unit_Diag_Area = 32-39
Value(1) = "Module 1"
Value(2) = "Module 2"
Value(3) = "Module 3"
Value(4) = "Module 4"
Value(5) = "Module 5"
Value(6) = "Module 6"
Value(7) = "Module 7"
Value(8) = "Module 8"
Value(9) = "Module 9"
Value(10) = "Module 10"
Value(11) = "Module 11"
Value(12) = "Module 12"
Value(13) = "Module 13"
Value(14) = "Module 14"
Value(15) = "Module 15"
Value(16) = "Module 16"
Value(17) = "Module 17"
Value(18) = "Module 18"
Value(19) = "Module 19"
Value(20) = "Module 20"
Value(21) = "Module 21"
Value(22) = "Module 22"
Value(23) = "Module 23"
Value(24) = "Module 24"
Value(25) = "Module 25"
Value(26) = "Module 26"
Value(27) = "Module 27"
Value(28) = "Module 28"
Value(29) = "Module 29"
Value(30) = "Module 30"
Value(31) = "Module 31"
Value(32) = "Module 32"
Value(33) = "Module 33"
Value(34) = "Module 34"
Value(35) = "Module 35"
Value(36) = "Module 36"
Value(37) = "Module 37"
Value(38) = "Module 38"
Value(39) = "Module 39"
Value(40) = "Module 40"
Value(41) = "Module 41"
Value(42) = "Module 42"
Value(43) = "Module 43"
Value(44) = "Module 44"
Value(45) = "Module 45"
Value(46) = "Module 46"
Value(47) = "Module 47"
Value(48) = "Module 48"
Value(49) = "Module 49"
Value(50) = "Module 50"
Value(51) = "Module 51"
Value(52) = "Module 52"
Value(53) = "Module 53"
Value(54) = "Module 54"
Value(55) = "Module 55"
Value(56) = "Module 56"
Value(57) = "Module 57"
Value(58) = "Module 58"
Value(59) = "Module 59"
Value(60) = "Module 60"
Value(61) = "Module 61"
Value(62) = "Module 62"
Value(63) = "Module 63"
Value(64) = "Module 64"
Unit_Diag_Area_End
;******** error location end ******************************
Unit_Diag_Area = 40-47
Value(1) = "-Module 1"
Value(2) = "-Module 2"
Value(3) = "-Module 3"
Value(4) = "-Module 4"
Value(5) = "-Module 5"
Value(6) = "-Module 6"
Value(7) = "-Module 7"
Value(8) = "-Module 8"
Value(9) = "-Module 9"
Value(10) = "-Module 10"
Value(11) = "-Module 11"
Value(12) = "-Module 12"
Value(13) = "-Module 13"
Value(14) = "-Module 14"
Value(15) = "-Module 15"
Value(16) = "-Module 16"
Value(17) = "-Module 17"
Value(18) = "-Module 18"
Value(19) = "-Module 19"
Value(20) = "-Module 20"
Value(21) = "-Module 21"
Value(22) = "-Module 22"
Value(23) = "-Module 23"
Value(24) = "-Module 24"
Value(25) = "-Module 25"
Value(26) = "-Module 26"
Value(27) = "-Module 27"
Value(28) = "-Module 28"
Value(29) = "-Module 29"
Value(30) = "-Module 30"
Value(31) = "-Module 31"
Value(32) = "-Module 32"
Value(33) = "-Module 33"
Value(34) = "-Module 34"
Value(35) = "-Module 35"
Value(36) = "-Module 36"
Value(37) = "-Module 37"
Value(38) = "-Module 38"
Value(39) = "-Module 39"
Value(40) = "-Module 40"
Value(41) = "-Module 41"
Value(42) = "-Module 42"
Value(43) = "-Module 43"
Value(44) = "-Module 44"
Value(45) = "-Module 45"
Value(46) = "-Module 46"
Value(47) = "-Module 47"
Value(48) = "-Module 48"
Value(49) = "-Module 49"
Value(50) = "-Module 50"
Value(51) = "-Module 51"
Value(52) = "-Module 52"
Value(53) = "-Module 53"
Value(54) = "-Module 54"
Value(55) = "-Module 55"
Value(56) = "-Module 56"
Value(57) = "-Module 57"
Value(58) = "-Module 58"
Value(59) = "-Module 59"
Value(60) = "-Module 60"
Value(61) = "-Module 61"
Value(62) = "-Module 62"
Value(63) = "-Module 63"
Value(64) = "-Module 64"
Unit_Diag_Area_End
;******** ID code ******************************************
Unit_Diag_Area = 48-55
Value(189) = "ID code: 189" ; DO
Value(190) = "ID code: 190" ; DI, thermistor, power- and segment terminals with diagnostics
Value(91) = "ID code: 91" ; AO
Value(125) = "ID code: 125" ; AO
Value(95) = "ID code: 95" ; AI
Value(127) = "ID code: 127" ; AI
Value(191) = "ID code: 191" ; motor starter, special function module
Value(220) = "ID code: 220" ; IC220BEM232, IC220BEM485
Value(223) = "ID code: 223" ; PCP-Modules AO4/8, Temp4/8
Unit_Diag_Area_End
;******** length code *************************************
Unit_Diag_Area = 56-63
Value(1) = "Data length: 1 word"
Value(2) = "Data length: 2 words"
Value(65) = "Data length: 4 Bit"
Value(129) = "Data length: 1 Byte"
Value(194) = "Data length: 2 Bit"
Unit_Diag_Area_End
;