TP 177A und Alarm_S

Zuviel Werbung?
-> Hier kostenlos registrieren
So hab ich gerade im Siemens forum gefunden, geht also nicht schade.

You have to enable Alarm_S classes. You do that under Settings --> Alarm settings--> Alarm procedures there you have an alarm_s tab. But be aware the old TP 170A suports alarm s but not the new TP177A. You have to switch to at least TP177B to get alarm s. If you consider to use alarms_s messages alot you have to get PDIAG it will make the configuration of the alarms so much easier.
 