@LowLevelMahn
4.) nastarjan have no PLC only the Danfoss FC102 Drive !
In Post #34 he tell that's the Adapter work with PLC S7-200 correctly, but at this time he have no PLC!
The Danfoss work with DPV1 Parameter Sequences to communicate with the MCT10 Software Suite.
To establish a DPV1 connection to a passive PROFIBUS Slave you need a PROFIBUS Master Class 2 , this mode is
available on the SIEMENS CP's when you set the Option "Is the Only Master in the bus".
So this doesn't look like a protocol problem but a Operating Mode Problem of the NetLink USB Compact!