Thread: Input register addresses in AXL F RS UNI for Modbus RTU

  1. #1
    Join Date
    10.09.2018
    Posts
    1
    Danke
    0
    Erhielt 0 Danke für 0 Beiträge

    Frage


    Zuviel Werbung?
    -> Hier kostenlos registrieren
    Dear all,

    I am using the AXL F RS UNI as a Modbus RTU slave in a project and am required to allocate a number of input registers at certain addresses for a Modbus Master. The problem is that the Modbus Master is expecting some data on input register with address 0, but in the standard library only addresses 2000-2999 are reserved for input registers. Addresses 0-1999 are reserved for Holding Registers, so I will receive an error when the Modbus Master will be expecting an input register at 0.

    Does someone know a way to "re-address" these hardcoded addresses, or know of another way to choose addresses freely? I am told that my option is to write a new function block just for this purpose, but I really want to avoid this as it would require a lot of time.

    Appreciate your help!
    Reply With Quote Reply With Quote Input register addresses in AXL F RS UNI for Modbus RTU  

  2. #2
    Join Date
    08.09.2010
    Location
    Blomberg
    Posts
    485
    Danke
    1
    Erhielt 88 Danke für 82 Beiträge

    Default


    Zuviel Werbung?
    -> Hier kostenlos registrieren
    It is not possible to read the input register of address 0 on the slave.
    You must make changes on the master side to read the input registers from address 2000 to 3000.
    There is no other option to read the input registers on the slave.
    PHOENIX CONTACT Deutschland GmbH
    Hotline: 05281-946-2888
    automation-service@phoenixcontact.com
    www.phoenixcontact.de

Similar Threads

  1. Replies: 1
    Last Post: 03.11.2016, 16:28
  2. Modbus RTU - Modbus Error Charrec Timeout
    By Klingone22 in forum CODESYS und IEC61131
    Replies: 8
    Last Post: 15.03.2016, 10:49
  3. Replies: 1
    Last Post: 07.01.2016, 18:04
  4. Replies: 1
    Last Post: 12.12.2014, 09:19
  5. Replies: 0
    Last Post: 03.04.2014, 14:26

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •