    no, because the symbol is saved offline and not in the db. siemens already don't use a realy symbol adressing.
    Yes but the symbols are stored in the Symbol table, not in the DB.

    but why will i lost all my symbols when i copy the online-db to the offline-db directly?
    Presumably because you overwrite the offline copy with the online one, instead of merging the two.

    Maybe they will be preserved, depending on whether Symbolic or Absolute priority is set, must try it out some time.

  2. #12
    Registriert seit
    06.10.2004
    Ort
    Kopenhagen.
    Beiträge
    4.626
    Danke
    377
    Erhielt 801 Danke für 642 Beiträge

    Standard

    If you open the project offline first, and then go online (from the STEP7 Manager), and then highlight the DB's that you want to save, and then select "PLC" .. "Uplad to PG", then the Actual Values will be uploaded and the Symbols and comments in the offline file will stay.

    I can think that there may be a problem if there is a timestamp conflict or something like that.
    Jesper M. Pedersen

  3. #13
    Registriert seit
    20.06.2003
    Ort
    Sauerland.NRW.Deutschland
    Beiträge
    4.850
    Danke
    78
    Erhielt 800 Danke für 543 Beiträge

    Standard

    yes, this will function. but if you have many db's you have many work.
    .
    mfg Volker .......... .. alles wird gut ..

    =>Meine Homepage .. direkt zum Download

    Meine Definition von TIA: Total Inakzeptable Applikation

  4. #14
    Anonymous Gast

    Standard


    Zuviel Werbung?
    -> Hier kostenlos registrieren
    Please find the solution what I reseive from SimonG in another forum:

    "Ok, for the case where the DB's are the same length, proceed as follows: Assume the DB you want to correct is DB1. Assume DB3 is currently not used.
    In the offline folder, create DB3 as a copy of DB1 (use cut/paste and then rename).
    Download DB3 to the plc.
    Write some program in the plc (say ob1) which copies the contents of DB1 to DB3.
    (e.g. if the DB's are 212 bytes long, use the following:
    CALL SFC 20
    SRCBLK :=P#DB1.DBX0.0 BYTE 212
    RET_VAL:=MW900
    DSTBLK :=P#DB3.DBX0.0 BYTE 212
    )
    Download to the plc. Make sure Mw900=0 to show the copy was ok.
    Remove the copy program from OB1 and download to the plc, (DB3 now contains a copy of what is in DB1 in the plc).
    Download DB1 to the plc.
    Write some program in ob1 to copy DB3 back to DB1
    (e.g.
    CALL SFC 20
    SRCBLK :=P#DB3.DBX0.0 BYTE 212
    RET_VAL:=MW900
    DSTBLK :=P#DB1.DBX0.0 BYTE 212
    )
    Download to plc. Make sure MW900=0 to show copy was ok.
    Remove the copy program from OB1 and download to the plc.
    Delete DB3.
    Db1 can now be copied from the online folder to the offline folder for your backup.
    For the DB's that are not the same length, you could use a similar procedure to the above, but the copy length will be the shorter of the two DB's.

    Hope this helps.
    "

    I can only say that sometimes, when the timestemp is the same is posible simply copy db from PLC to project and we keep symbols, coments etc. But if we have differences is impossible backup aktual data na keep symbols in DB

    regards
    Ed

Ähnliche Themen

  1. S7 Backup
    Von thomass5 im Forum Simatic
    Antworten: 3
    Letzter Beitrag: 08.09.2008, 10:07
  2. Backup von IPC für Serienmaschine
    Von godi im Forum PC- und Netzwerktechnik
    Antworten: 9
    Letzter Beitrag: 02.07.2008, 13:01
  3. Backup S7
    Von Percival im Forum Simatic
    Antworten: 12
    Letzter Beitrag: 25.01.2008, 11:28
  4. Backup OP7
    Von Nudelschinken im Forum HMI
    Antworten: 5
    Letzter Beitrag: 22.02.2006, 08:42
  5. op7 backup
    Von Unregistriert im Forum HMI
    Antworten: 0
    Letzter Beitrag: 15.02.2006, 10:23

Lesezeichen

Berechtigungen

  • Neue Themen erstellen: Nein
  • Themen beantworten: Nein
  • Anhänge hochladen: Nein
  • Beiträge bearbeiten: Nein
  •