Gentelmern, I am unable to get any guidance on this issue on my normal english forums. Siemens technical help line requires $300 US to address support on "Mature" products. I hope you can help

I have a customer with a KAMMANN bottle printer. The controller is a S5-105R. The only programmer I have available that might be of some use is a 740 PG II. I am trying to confirm that this programmer will be compatible with this controller. Sorry for the english on your forum. Hope someone can help. Thank you

Terry Peterson
 
Zuviel Werbung?
-> Hier kostenlos registrieren
Thank you Thomas. I did read that thread. The only direction I have found is the 740 PG manual states it will work with S5-90U to S5-155U but I have been told that the U version differs from the R version.
 
As far as i know, you need a PG605. There was an program for PG675 to read and convert S5 110 and 105 to 'normal' S5.
 
Thank you all so much for sharing your information. At this point I am understanding that the 740 PG II programmer will not function with the S5-105R controller. I see that even the PG605 hand held programmer comes in both U and R series. Can anyone elaborate on the difference between the U and R series controllers that they need different programmers?
 