F360:B12B
Configuration data inconsistent with the parameterization of the I/O device
Cause
Overview Page 28 of 158
file:///C:/Users/Hotline/AppData/Local/Temp/~hh8F89.htm 05/12/2019From the SIMOTION viewpoint, during the online comparison of the configuration data of the project with the parameterization of an I/O device (e.g. drive, e
(The associated expected value of the device parameter for the SIMOTION project is displayed in the note.)
- Inconsistency at a drive (TO axis)
Reason 100: T_mapc (HW Config) not identical with the servo cycle, note: Servo cycle
Reason 110: P922 Incompatible telegram type
Reason 111: P924 Inconsistent PZD no. parameterization for pulse enable signal
Reason 112: P924 Inconsistent bit no. parameterization for pulse enable signal
- Inconsistency at an encoder (TO axis, TO external encoder)
Reason 200: T_mapc (HW Config) not identical with the servo cycle, note: Servo cycle
Reason 210: P922 Incompatible telegram type
Reason 211: P979 Attached encoder in not an absolute encoder, note: 0
Reason 212: P979 Inconsistent number of increments per revolution
Reason 213: P979 Inconsistent fine resolution for Gx_XIST1, note: Shift factor
Reason 214: P979 Inconsistent fine resolution for Gx_XIST2, note: Shift factor
Reason 215: P979 Inconsistent number of revolutions of the absolute encoder
Reason 216: P65001 Unsupported format of the actual speed value, note: N2/N4
- Inconsistency at a SINAMICS DO1 with standard telegram 39x
Reason 310: P922 Incompatible telegram type
Reason 311: Pxxx Duplicated configuration of a GPIO for SINAMICS and SIMOTION, note: Bit number
Reason 312: P728 Direction configuration of a GPIO not unique, note: Bit number
Reason 320: P680 GPIO not configured as measuring input or in the wrong measuring input channel, note: Bit number
Reason 321: P680 measuring input channel not configured, note: Channel number (P680 index)
- Inconsistency at a TM15/TM17 High Feature
Reason 402: P4099 value for the cam output delay too small, note: Delay time
Reason 420: Measuring input not parameterized as input in P4029 or as time in P4049, note: Bit number
Reason 430: Output cam not parameterized as output in P4029 or as time in P4049, note: Bit number
Remedy
Check whether the false setting in the parameterization of the I/O device or in the configuration of the SIMOTION project is warranted.
- For reasons 1xx and 2xx, the configuration data of the TO contains different settings for the drive and the encoder configuring. Note that the named P9xx
- For reasons 3xx and 4xx, the FastIO configuration contains inconsistent entries compared to the parameters of the corresponding SINAMICS DO. Delete the cu