Hello all,
I have a CX5130 and I am trying to open a archive file which is from another PLC (CX-9020). There is no change in any of the I/O terminals (EL 1809, EL2809) or with the motor terminals (EL7041) , just the PLC has changed. Now, When I open the archive file, I see everything is same as previous (NC axis, Terminals, variable links, mappings, etc). I did the network adapter search to find the new EtherCAT device (CX5130) and found it. Now, when I try to run the program, I see the MC_power enable, positive, negative, doesnt turn TRUE.

My question is: 1. Is there something I missed to do (assigning mappings to NC / plc) ? I can see all the inputs and outputs are linked .
2. I am confused, because when I remove the Link to PLC, I can move the motors manually (no problem with the wirings)
3. When I "link to PLC" some variables, I have a warning LED llight up on my motor terminals (documentation tells the error is because of motor connection, or high temperature)

Or is it just a programming error? (the program was running perfectly before, so I guess there should be a assigning mappings error that I have made.) Please help. Thank you.
 
Hi,
did you check the configuration of the EL7041 after you scan the network adapter? Maybe they get lost after scan and now on default.
 
Hello all,
just figured out what was causing the problem. VISU was password protected (CX9020) and the login details were not working on the CX5130. In the user management settings, there is an option to "download the user to device". When the user is downloaded to the new device, everything works fine. Anyways, Thank you all for your help. Hope this information helps. Cheers.

Karthik
 